Pramac GBW30P Encl Diesel Genset w/Perkins Eng - Answered Questions & Fixed issues

0helpful
4answers

Its 230kvaperkins generator it starts normally,but

Low frequency means the RPM of the motor has fallen off.

Check your fuel is NOT contaminated or fuel filters plugged.

Further tests should focus on the govenor system. Possibly it fails when engine gets hot. the frequency is directly proportional to the engine speed.
10/10/2022 2:39:56 PM • Pramac GBW30P... • Answered on Oct 10, 2022 • 395 views
0helpful
5answers

The gent set is Perkins 135 KVA after overhauled

Check the fuel solenoid is getting power. It may be locked out by loow lube oil pressure and other things.

ALSO when restarting a diesel one OFTEN must "bleed" the fuel lines at each injector... same as when one inadvertently runs a diesel out of fuel. Crack the connectors at the injectors and crank till fuel comes out and tighten each one. Yes, it is a pain...
12/7/2019 6:36:49 AM • Pramac GBW30P... • Answered on Dec 07, 2019 • 663 views
0helpful
3answers

Genset does not start ,

what safety caused the alarm. if you cant restart it, it may be cause the problem that originally shut the engine down has not been fixed, it could be water level, low oil, high water temp, low fuel,over voltage, all of the above are probably run through the safeties. over volt, and water temp would probably clear its self after it sat a while. try turning off power to panel. for a couple minutes and see if it will reset, if not check water level. and oil levels
12/6/2019 7:28:35 AM • Pramac GBW30P... • Answered on Dec 06, 2019 • 692 views
0helpful
2answers

500kva 380 volt diesel generetor

make sure gen isnt stopt on protection overtemperature or oil level or coolant level. try to bridge protections one by one to find the course. first make sure all fluids are on level and coolers are clean. fanbelt tension and coolantthermostat can also be wrong.
12/6/2019 7:21:27 AM • Pramac GBW30P... • Answered on Dec 06, 2019 • 273 views
0helpful
3answers

How ican fix the high temprature problem

Water level, good thermostat, good water pump, fan working? All things to check.

Sometimes an airlock will prevent water circulation

ALSO verify your temp gauge and sensor is working correctely. A failure of these may appear as high temp and even shut machine down if the sensor is bad.
1/22/2019 6:01:43 AM • Pramac GBW30P... • Answered on Jan 22, 2019 • 409 views
0helpful
1answer

We have a Perkins diesel engine in a

The leakage fault of diesel generator is usually caused by the injection of corrosive coolant or seawater into the water radiator of the diesel engine. Cause of failure: 1. The cooling water added to the cooling water radiator by operator is seawater, which results in the damage of internal waterway and external interface of diesel engine. Therefore, the use of diesel engines must be strictly in accordance with the provisions of the diesel engine operation. 2, the operator feed water radiator in the addition of strong anti-freeze corrosion, resulting in diesel engine waterway parts damage. Troubleshooting methods: 1.Disassemble damaged parts of diesel engine, replace damaged parts of diesel engine after washing water radiator and inner waterway of block with fresh water. 2, after assembly, adjustment, test machine found that the diesel engine returned to normal, the fault was eliminated.
1/22/2019 5:57:26 AM • Pramac GBW30P... • Answered on Jan 22, 2019 • 252 views
0helpful
3answers

Can u esplain about trouble shooting in diesel

my 500 kva diesel generetors dosnt work since mornning its workes after 4 houres when the weather changed
12/22/2018 8:07:14 AM • Pramac GBW30P... • Answered on Dec 22, 2018 • 471 views
0helpful
1answer

Stop failure alarm on genset

1: Check if the alarm is stopped, a, low oil pressure b, high water temperature c, overspeed, etc.; 2: Check if it is overloaded, whether the inlet and outlet pipes are unblocked 3: Check if the parts are broken or loose, and check if the fuel tank is short of oil. 4: Check if the fuel injection pump is damaged 5: Check the speed sensor, electronic speed control board, actuator, etc.
12/22/2018 7:55:23 AM • Pramac GBW30P... • Answered on Dec 22, 2018 • 3,271 views
0helpful
3answers

Diesel mixed with oil in the sump

You run again the generator but before running, check & mark the oil level. Then stop the generator & wait until the oil settle to the bottom of oil pan. Check the oil level again & if the oil level is higher than the marking before that's means you have an engine gasket leak.You need to replace that gasket.
12/18/2018 6:05:59 AM • Pramac GBW30P... • Answered on Dec 18, 2018 • 805 views
0helpful
1answer

What can i do to reset generac 0058750 genset under voltage alarm?

Did you have a auto controller? With the switch set to AUTO, the engine may crank and start at any time without warning. Such automatic starting occurs when utility power source voltage drops below a preset pevent or during the normal exercise cycle. To prevent possible injury that might be caused by such sudden starts, always set the switch to OFF and remove the fuse before work. Ing on or around the generator or transfer switch.
12/7/2018 6:14:54 AM • Pramac GBW30P... • Answered on Dec 07, 2018 • 347 views
0helpful
1answer

Where is the rpm sensor on a genset generator

The distance between the sensor and the diesel generator flywheel is too far or too close (generally this distance is approximately 2.5 + 0.3 mm). If the distance is too far, it may not be able to sense the signal. If it is too close, it may damage the working surface of the sensor. Due to the high-speed operation of the flywheel, radial (or axial) turbulence occurs. The distance is too close to pose a great threat to the safety of the sensor. It has been found that several working faces of the probe have been scratched. According to practical experience, the distance is generally about 2mm, which can be measured with a feeler gauge.
11/21/2018 3:26:33 AM • Pramac GBW30P... • Answered on Nov 21, 2018 • 243 views
0helpful
3answers

What is the size Battery (cranking amp) needed for

If the unit has a battery box, measure it and get the largest size that will fit and of course the correct voltage. Diesels take a lot to crank.

You can search battery sizes on the internet for physical size. NAPA has a pretty good selection.
9/27/2018 9:04:43 AM • Pramac GBW30P... • Answered on Sep 27, 2018 • 649 views
0helpful
2answers

Genset can not pick up once main electricity

The controller circuit card needs to be replace. This is
the one that senses if and when power is shut off. This
will automatically start the engines.
9/27/2018 8:43:04 AM • Pramac GBW30P... • Answered on Sep 27, 2018 • 249 views
0helpful
1answer

Perkins 20 kva diesel generator runs and stops in

Ensure any engine control switch is set to the run position, with the load disengaged. Manually set the air shut off valve (if fitted) to the run position (see Fig. 18), Turn the key switch to the start position, which will energize the solenoid allowing the engine to crank over for a few seconds then start. Check the instrument panel is showing normal running oil pressure, and the ammeter for charge to the engine batteries. Allow the engine to run for five minutes checking the instruments are reading correctly. Stop the engine and check the oil and coolant levels, replenish if necessary. https://www.dieselgeneratortech.com/generator-sets/normal-starting-procedure-of-Perkins-generator-set.html
8/21/2018 6:33:33 AM • Pramac GBW30P... • Answered on Aug 21, 2018 • 289 views
0helpful
2answers

Pramac 25 kva perkins encl diesel genset will not start red light on triangle on check list

Hello. Maybe you have solved your problems. But I still want to share the helpful article to you. https://www.dieselgeneratortech.com/diesel-generators/why-diesel-generator-fail-to-start.html We are Perkins diesel generator OEM. Can provide 22KW to 2200KW diesel generator set with Perkins engine. https://www.dieselgeneratortech.com/perkins perkins diesel generators-n5v1fnwbur1qlbncsxenjidv-1-0.jpg
8/9/2018 6:52:39 AM • Pramac GBW30P... • Answered on Aug 09, 2018 • 590 views
0helpful
2answers

If the gen set battery is good and yet the gen set

check for dirty or corroded connections or loos weir's
8/7/2018 3:04:13 AM • Pramac GBW30P... • Answered on Aug 07, 2018 • 355 views
0helpful
1answer

How do i align the timing gear on my perkins dk

Timing gears? have you pulled it that far apart? On timing gears there are usually stamped onto the gears a small dot. lign them up. Not sure why tore down so far? If you take off the diesel pump align the timing marks in the small window plate first else you will be in a mess.
11/17/2013 4:21:38 PM • Pramac GBW30P... • Answered on Nov 17, 2013 • 359 views
0helpful
1answer

ELECTRICITY PRESENTS BUT GENERATOR START IN AUTO MODE

You have the remote control wires incorrectly connected either at the ATS or on the generator control panel, disconenct from both ends and ohm them to make sure they are not shorted between. Then reconnect them at the generator end only. Then join them together manually, of the gen starts and stops when taken apart, the problem is in the transer switch, or incorrect terminated
11/16/2013 6:50:22 PM • Pramac GBW30P... • Answered on Nov 16, 2013 • 273 views
0helpful
1answer

Perkins 3 cylinder powered pramac generator

Start looking at your safety circuits.

1. High water temp
2. Low Oil
3. Low water etc...

From the manual these are the protection circuits.

• Engine protection: low oil pressure, high engine temperature.
• Genset protection: under/over voltage, overload, battery charger failure, battery voltage out of limits,
under/over frequency, start failure.
• Circuit breaker protection: IV poles.
• Differential protection.


Any one of them will trip the fuel relay closed. What you may be able to do is disconnect one at a time each protection circuit and see when the fuel relay opens. (Make sure to reconnect each one if it had no effect on the fuel solenoid)

Once you isolate which circuit it is in then you can chase wires or change the bad switch.

Thanks for choosing FixYa.

Kelly

6/26/2010 1:01:59 PM • Pramac GBW30P... • Answered on Jun 26, 2010 • 1,144 views
0helpful
1answer

Boat engine will not start even with new battery.

This may sound over simplified but..... old battery cables corrode onboth ends so you have less amperage carried by the cables. (i.e. fewer strands of copper trying to carry more amperage than they are capable of. The next time you do a start cycle place your hands on the battery terminals one at a time and check to see if they are HOT to the touch. Also do the same thing for the chassis ground and the terminal lug at the starter. ANY hot terminal is a sign the cable has broke down either from age/vibration wear or corrosion. If you suspect the battery cables are bad get a VERY GOOD set of jumper cables (2 sets connected together if necessary) and do a direct from the battery to the starter connection. This is loads of amperage so be very careful and DO NOT do this alone. But, if the starter spins faster you have battery cable problems.

IF you have an external to the starter relay that too can cause the problem due to worn / defective contacts.

I will watch for any responses.

Thanks for using FixYa.

Kelly
6/26/2010 7:20:17 AM • Pramac GBW30P... • Answered on Jun 26, 2010 • 239 views
Not finding what you are looking for?
Pramac GBW30P Encl Diesel Genset w/Perkins Eng Logo

39 questions posted

Ask a Question

Usually answered in minutes!

Top Pramac Electrical Supplies Experts

littlewheel

Level 2 Expert

122 Answers

Ngoro

Level 3 Expert

3521 Answers

john h

Level 3 Expert

29494 Answers

Are you a Pramac Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...