Inverter KEB COMBIVERT F5 - Answered Questions & Fixed issues

0helpful
1answer

I have a keb F4 how i can have the factory setting

Registered users on the KEB website have access to the manuals which will provide details on programming the inverters.
8/2/2022 9:10:39 AM • Inverter KEB... • Answered on Aug 02, 2022 • 2,834 views
0helpful
1answer

I have a keb inverter for c51 carding machine new I need to make it start

I would guess that this is off of a Rieter machine (C51 Carding Machine). They would be your best source of information. Verify that the unit is properly programmed and that the control wires are correct.
7/25/2016 7:23:06 PM • Inverter KEB... • Answered on Jul 25, 2016 • 514 views
0helpful
1answer

What does OL2 fault in KEB drive indicate?

Too much current is being required with the motor shaft not rotating. This is most likely a parameter adjustment issue with the motor data, torque limits and protective functions. Possible motor issue as well.
7/25/2016 7:20:32 PM • Inverter KEB... • Answered on Jul 25, 2016 • 1,044 views
0helpful
1answer

What is no_PO error

no_PU = No power unit. 24Vdc is being supplied to the control card with no AC voltage (230 or 400) being supplied to L1/L2/L3. Verify AC voltage is present at L1/L2/L3. *If not present, apply voltage and no_PU should clear. *If present and unit still no_PU, there is a problem with the power stage. At that point unit should be replaced or repaired.
7/25/2016 7:15:44 PM • Inverter KEB... • Answered on Jul 25, 2016 • 770 views
0helpful
1answer

How to save the parameters in KEB F5

Here is how to use the keypad. If a decimal shows up after the value is changed, enter must be pressed to save the value. Also insure that the inverter is not enabled or in nOP status.

20ce52e8-a69b-4f90-9955-42227d13512f.jpg
7/25/2016 7:09:22 PM • Inverter KEB... • Answered on Jul 25, 2016 • 1,429 views
0helpful
1answer

Vmi fault coming up

Vmi is not a KEB fault code.
6/3/2015 2:48:31 PM • Inverter KEB... • Answered on Jun 03, 2015 • 321 views
0helpful
1answer

General fault 142

The does not appear to be a KEB error code.
6/3/2015 2:47:45 PM • Inverter KEB... • Answered on Jun 03, 2015 • 327 views
0helpful
1answer

General fault 142error

This does not appear to be a KEB error code. If this code is on on your HMI, contact the machine manufacture to determine what this error means.
6/3/2015 2:45:19 PM • Inverter KEB... • Answered on Jun 03, 2015 • 358 views
0helpful
2answers

Always showing alarm EOC,EOP

The system that you described is a closed-loop system. The inverter tells the motor what to do and the encoder send information back to the inverter to verify the operations. With out knowing part# and serial number of the unit in question, I do not know exactly which inverter you are having problems with. With E.OC error, there is a lot of current demand on the inverter. This could mean a short in the motor, motor leads, connections or inside of the inverter. This could also be caused by the encoder feedback loop being defective. If the inverter tells the motor to run at 1000rpm and the feedback tells the inverter it is only running at 5rpm, the inverter will send out more current to get the motor up to speed. Since you are getting multiple errors, there could be other internal problems with the inverter especially if the unit is old and contaminated internally.
6/3/2015 2:42:26 PM • Inverter KEB... • Answered on Jun 03, 2015 • 1,764 views
0helpful
1answer

I have a KEB combivert F5. The parameter ru 00 shows nop even if i give switching to terminal 16 for control release.Please help.

This may be due to the inverter waiting for an ST signal via buss communications. What is the part # of the unit in question? The inverter is recognizing that terminal 16 is going active but still waiting for another command to enable the inverter.
2/18/2017 10:37:29 AM • Inverter KEB... • Answered on Feb 18, 2017 • 1,956 views
0helpful
1answer

The inverter not work and all signals good

Verify the mains voltage at terminals L1/L2/L3. If it is present but the inverter does not power up, there is most likely an internal problem. What is the part# of the unit in question?
4/18/2016 1:06:14 PM • Inverter KEB... • Answered on Apr 18, 2016 • 637 views
0helpful
1answer

We have KEB Combivert F5 drive Matno. 15F5C1E-350A Version. drive is installed in machine and is not working right now.i want to run the drive in Manual mode to test it.

if the display says LS, it means you are missing the speed and direction command. Via the keypad, provide the direction and then the speed.
3/9/2015 1:44:37 PM • Inverter KEB... • Answered on Mar 09, 2015 • 857 views
0helpful
2answers

Keb inverter f5 error e.pu

General powericon1.png stage failure. Most likely will need to replace the power stage or inverter.
2/6/2015 3:06:56 PM • Inverter KEB... • Answered on Feb 06, 2015 • 2,923 views
0helpful
1answer

After a service to the motor bearing that also touch the encoder. when I switch on the power the motor is already running.at first it should be on stop position

The inverter will only do what it is being signaled to do. Check the control signals to the inverter and make sure that they are correct. Since there is an encoder on the system, I will assume that this is a closed loop system. Try to home the system.
11/25/2014 8:48:42 PM • Inverter KEB... • Answered on Nov 25, 2014 • 116 views
0helpful
1answer

We got EUPH warning. the motor running in wild mode. how to fix

E.uPh due to the ripple detection of the DC bus. This is typically caused by a missing phase on the input side of the inverter. Measure your mains voltage L1-L2, L2-L3, L1-L3 and L1-ground, L2-ground, L3-ground to verify that your supply voltage is balanced and withing the rated specifications. If the applied voltage is good then there is a problem with the input stage or the DC bus and the unit will need to be repaired or replaced.
11/25/2014 8:46:23 PM • Inverter KEB... • Answered on Nov 25, 2014 • 506 views
0helpful
1answer

Keb f5 e puch

Look under the E.puch tip section.
9/3/2014 2:17:25 AM • Inverter KEB... • Answered on Sep 03, 2014 • 717 views
0helpful
1answer

I fit a new keb f5 inverter which parameter set to

Pretty general question. If it is a replacement inverter, best source would be to upload parameter values from original inverter with the COMBIVIS software.

Otherwise I would suggest downloading the manual from the KEB web site.
9/3/2014 2:14:17 AM • Inverter KEB... • Answered on Sep 03, 2014 • 265 views
0helpful
1answer

Manuals inverter keb

These can be obtained from the KEB web site.
9/3/2014 2:09:41 AM • Inverter KEB... • Answered on Sep 03, 2014 • 154 views
0helpful
1answer

Inverter KEB COMBIVERT F5 parameter

The manual that came with the inverter has instructions on how to go from mode to mode.

If you do not have the manual, these can be downloaded from the KEB web site.
9/3/2014 2:08:38 AM • Inverter KEB... • Answered on Sep 03, 2014 • 463 views
0helpful
1answer

Ow do i fix error 59

If you are talking about error code 59 then the error is E.HybC. E.HybC means that the feedback card on the inverter has been changed. You must confirm the change at parameter ec.0 or ec.10. The inverter reads the value from the feedback card so all you have to do it hit enter to confirm the value. If you have not changed the feedback card but the error continues to come back then there is a problem with the feedback card or the control card.
8/22/2014 4:33:53 PM • Inverter KEB... • Answered on Aug 22, 2014 • 339 views
Not finding what you are looking for?
Inverter KEB COMBIVERT F5 Logo

132 questions posted

Ask a Question

Usually answered in minutes!

Top Inverter Electronics - Others Experts

Brad Brown

Level 3 Expert

19187 Answers

Ngoro

Level 3 Expert

3523 Answers

john h

Level 3 Expert

29494 Answers

Are you an Inverter Electronics - Other Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...