20 Most Recent True 19 cu. ft. / 538 liter Commercial Freezer T-19F Questions & Answers

0helpful
1answer

110v surge protector that conserves power for freezer

A surge protector for a freezer is a good idea. To conserve energy? On paper it looks good but seriously only real savings are on bigger equipment.
11/4/2014 6:20:25 AM • True 19 cu. ft.... • Answered on Nov 04, 2014
0helpful
1answer

Freezer runs frequently, we don't open it very

Hi,
No timer...it goes on and off on a t-stat...if it is running alot it is not cooling properly...
Many times a freezer and/or refrigeratordo not work right because of a dirty condenser coil...there are also many otherthings that can go wrong. If you are hearing a clicking or buzzing then check out thelast two tips.

If your refrigerator is running but warm, then...

Check out this tip that I wrote about that... it is a great place to starttrouble shooting your unit...and something that you can do rather then callinga repair person to do a simple thing for you...

Refrigerator Condenser Coil Cleaning Refrigerator Repair

Refrigerator Troubleshooting Refrigerator Compressor

Refrigerator Compressor Start Capacitor and Start Relay


heatman101
9/18/2010 3:08:04 PM • True 19 cu. ft.... • Answered on Sep 18, 2010
0helpful
1answer

Door swing

yes any door swing can be reversed.take a good look and you will see the screws covered up with plastic covers .the door has to be removed first but check it out and you will see its not a big job get everything ready and it can be done within 10 minutes.adrian,,,,
6/29/2010 2:04:01 AM • True 19 cu. ft.... • Answered on Jun 29, 2010
0helpful
1answer

What could cause an evaporator coil to freeze up

Hello
Could be low on freon,i belive this model uses 134A.

So the suction pressure should be 31 to 35 psig,for a temp of 36 to 40.f

Also check the defrost timer and the door seal. The eveap should have a drain line on it, make sure this is working and not plugged.
4/7/2010 1:21:31 PM • True 19 cu. ft.... • Answered on Apr 07, 2010
0helpful
1answer

Freezer begun tripping our 20 amp breaker for some reason

ok hi there i viewed the specs for this freezer
http://www.truemfg.com/catalog/servlet/com.apsiva.servlet.HomeServlet
this unit must be plugged into a 120v outlet with a 15amp circuit breaker dedicated (nothing else should on this circuit) so all by itself. you have to check the voltage outlet where you plug in. you must have at least 115v or better (125v the most) if you have less then 115v it will cause damage. ok you went and checked all this out and everything is 15amp with 115v or better and it still trips breaker.
ok the running amps is 6.8 amps so to blow the circuit you need 15 amp which is too high.
i suggest you call a refrigeration guy because he will be able to determine if the problem is the compressor (which has a 4 year warranty with truemfg.com only in the USA) or something else. Usually but not 100% what would make a freezer like yours to blow the fuse is the compressor. if it overheats it will do this, if there is a sudden high pressure within the system it will do it, if you have a condenser fan that is not running at proper speed it will do this...
the problem cannot be pin pointed understand please... you have to babysit it, watch for changes in the refrigeration system and the running compressor amps, voltage drops ( this will cause high amps) etc...
Refrigeration is not easy and alot of tech stay away... so those who stick it out make money cause you have 2 choices: buy another one and pay big bucks to get it fixed. at least see if you can find someone to come over (for like $40 - $60) and tell you exactly whats wrong with it... whew... hope this was helpful and not confusing...sorry
4/4/2010 4:56:33 AM • True 19 cu. ft.... • Answered on Apr 04, 2010
0helpful
1answer

Condensing unit terns off but won't come back on

If it runs, turns off, then tries to restart and kicks breaker, look for bad start components. Check start relay, start capacitor. It may be trying to restart too quickly and the compressor over amps and breaker trips. The system needs to have at least 3 minutes of off time before trying to restart. This allows the pressures in the system to balance enough so the compressor can overcome the high side pressure and start. I've seen where people turn the control up and down very quickly causing the compressor to over amp and trip breakers and over loads.
Hope this gets it for you.
10/24/2009 12:53:21 AM • True 19 cu. ft.... • Answered on Oct 24, 2009
0helpful
1answer

Wiring daigram

Go to "truemfg.com". You can fill in your info on the home page and gain access to a 24 hour, on-line tech support. Worth a try.
3/7/2009 4:21:58 AM • True 19 cu. ft.... • Answered on Mar 07, 2009
0helpful
1answer

True T-49F 55? 2 Door Solid Reach In Freezer. How to solve error code E1 on freezer Tru T49f?

Question edited for clarity. Question moved to maker category. Thermostat Probe Error

E1 error on a true freezer. True Freezer, 5yrs. Just

JustAnswer https://www.justanswer.com > Appliance Repair Mar 6, 2022 - Ok. The E1 error code indicates a thermostat probe failure. 1 answer · Top answer: Hi, welcome to JustAnswer. My name is***** am a ticketed HVAC and refrigeration technician with ...

True Refrigeration Troubleshooting

Parts Town https://www.partstown.com > resource-center > guides P1 Alarm/ E1 Code. What does it mean? - This indicates a thermostat probe failure. "P1" displays on units with Dixell electronic controls. "E1" . ..
4/12/2024 3:24:01 PM • True Freezers • Answered on Apr 12, 2024
0helpful
1answer

True T-23F Single door freezer. My freezer isn't running?

Question edited for clarity and better English. Low on Refrigerant Gas. You need a refrigeration engineer.
10/12/2023 3:39:09 AM • True Freezers • Answered on Oct 12, 2023
0helpful
1answer

True T-49F 55", 2 Door Solid, Reach In Freezer. It sounds like it is one but it is not getting even cool? True Freezer.

Question edited for a lot more clarity. Question moved to True Freezer category. You need a refrigeration engineer. It sounds like is has a leak and needs topping up with refrigerant gas. Things that also need checking, circulation fan working and that the defrost timer and defrost heater, and electronic thermostat are working correctly. Refrigeration is not a handyman job. ..
4/14/2023 4:33:18 AM • True Freezers • Answered on Apr 14, 2023
0helpful
1answer

My true freezer will not freeze...everything turns on but tye fan inside....please help!!!

Your fan it's either defective, Or your unit is frozen up and the fan is stuck in ice. Unplug it defrost it take off the panels and see if the motor's any good .
6/2/2022 5:08:58 AM • True Freezers • Answered on Jun 02, 2022
0helpful
2answers

No door heat

The Mulluen heaters will be Built into the frame not in the door.
1/10/2022 5:01:22 PM • True Freezers • Answered on Jan 10, 2022
0helpful
1answer

I have true freezer t-19 that's not getting cold.it turns on but that's about it

we are not freezer repair tech , call one local to you
5/31/2021 9:44:39 AM • True Freezers • Answered on May 31, 2021
0helpful
1answer

On freezer True T-23, the compressor works around 5 minutes and turn off for around 5-6 minutes and start again for another 5 minutes. I need help

That is what it is supposed to do. It is called cycling and switches off when the set temperature is reached. It is a commercial freezer, so if the door opened and closed often, that is normal?Commercial freezers and fridges have an item called a 'Clixon' that cuts power in the case of the compressor overheating. When was the last time the fins on the compressor coils were cleaned? Could also be a bad door seal letting cold air escape. When you close a freezer door on a unit like that, it should be really hard to open straight afterward due to the suction. Could be a faulty thermostat. Turn the temperature to the warmest setting and see if it still does it? If it does, you need a new thermostat.I just retired after 52 years in catering.https://www.katom.com/598-T23F.html?gclid=CjwKCAiArbv_BRA8EiwAYGs23PKtEzF60_OMVNpHXBlGjHQNdpp0pDZsu0G0lFLqVy2p4qIybG9n8xoCwEMQAvD_BwE..
1/1/2021 9:38:12 PM • True Freezers • Answered on Jan 01, 2021
0helpful
1answer

Why is jenn air jcd2389ge hot around front freezer door frame?

The heat at the opening of refrigerator is usually a sign the condenser coils are dirty. Check the condenser coils for a restriction underneath the unit. Dirty condenser coils will cause poor air flow over the coils and compressor. Poor air flow will cause a lot of problems, including overheating the compressor, the refrigerant and the copper lines. This will destroy your sealed system. The coils need cleaning at least once a year, more often if you have pets.
I couldn’t determine if your unit has an “energy saver” setting. If so, turn it on. Not all refrigerators have energy saver. This is on units with emilion heaters in the wall around the door gaskets. The heaters are to eliminate condensation around the door. Turning ON energy saver turns OFF those heaters. You should notice a change quickly if it’s the heater causing the heat, that is, if you have that model.
Cleaning the coils will need a day or two to allow things to cool down before you notice a change in the heat around the door.
7/29/2019 4:27:08 AM • True Freezers • Answered on Jul 29, 2019
0helpful
1answer

Can the temperature be adjusted on the true GDM-49F

https://download.partstown.com/is-bin/intershop.static/WFS/Reedy-PartsTown-Site/-/en_US/manuals/TRUE-GDM_iom.pdf Here is the site for the ops manual. should walk you thru how to do temp adjustments.
11/19/2018 11:10:04 PM • True Freezers • Answered on Nov 19, 2018
0helpful
1answer

True 49f fans stopped running. Compressor still runs. Fixes? Troubleshooting steps?

I am assuming you are relating to the evaporator fan(s) not running. If this is the case, some units have a 'Klixon" type thermostat in the evaporator so when the evaporator coil temp reaches a predetermined temperature, the fans come on. You may have a bad "Fan Delay" (Klixon) or the coil is not reaching the proper temp to activate it to turn on the fans. I would check the wiring diagram on the unit for this part to see if this unit has it in the system.
6/12/2018 12:18:22 AM • True Freezers • Answered on Jun 12, 2018
Not finding what you are looking for?
True 19 cu. ft. / 538 liter Commercial Freezer T-19F Logo

10 questions posted

Ask a Question

Usually answered in minutes!

Top True Freezers Experts

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66830 Answers

Are you a True Freezer Expert? Answer questions, earn points and help others

Answer questions