The Rheem water heater uses 4500 Watt elements
Check label on side of any appliance to see electrical rating details
2 element tank with two 4500 watt elements is still a 4500 watt appliance since both elements are never ON at same time.
Volts x amps = watts
amps = watts divided by volts
amps = 4500 divided by 240Volts or 220Volts
amps = 18.75
Your water heater uses 18.75 amps to 20.45 amps
Your 25 amp breaker should only carry 80% of rated value
25 amps x 80% = 20 amps.
So your water heater breaker is correctly sized.
You should have a 10 gauge wire going to this water heater.
12 gauge wire is a bit undersized for 4500 Watt water heater
Feel the water heater wire to see if it is warm.
If the main breaker is getting hot when 20 additional amps are being used by the water heater.
1) The house is using more amps than your 100 amp main can carry
Using the formula, 100 amps x 80% = 80 amps for the main breaker
Add up your total amp draw.
For example if your 3500 watt oven is ON, it draws 16 amps.
If your 5000 Watt electric heater is on, it draws 23 amps.
Your 1500 Watt 120V microwave draws 12.5 amps.
Add these numbers up plus your water heater, and it comes to 71 amps.
71 amps is getting close to the max 80 amp, but it's not over.
Now if you have a pool pump and and hot tub and a table saw going, the main breaker could be overdrawn.
2) To solve the problem short-term, you can put a timer on the water heater and use it only when needed.
http://waterheatertimer.org/Compare-13-electric-water-heater-timers.html3) The main breaker is bad and needs to be replaced.
If you need help figuring circuits or timers, add a comment and I will help