You installer configuration is set for Celsius instead of Fahrenheit.
I'm assuming that's Celsius. what is the model number?
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
SOURCE: Can Movincool classic plus 26 AC set the air temperature at below 70 degree F?
aircons normally pull down to approx. 17 degree celcius.and heats to approx 30 degree celcius. most of the time you need to simply clean the condenser properly and to make sure fans are in good order.
SOURCE: Oven temperature only gets to within 20-25 degrees of temp. set
next to last page in your manual
Adjusting Oven Temperature
Oven temperature has been factory calibrated and tested. If
oven consistently over or under cooks food, adjust thermostat.
Oven temperature can be increased or decreased 35°F. To
avoid over adjusting oven, move temperature 5°F each time.
1. Push BAKE pad.
2. Press + pad until an oven temperature greater than 500°F
shows in display.
3. Immediately push and hold, approximately 5 seconds,
BAKE button until “00” appears.
4. Press + or - arrow pad to adjust oven temperature.
• To increase oven temperature (for a hotter oven), Press
pad until a positive number appears in display.
• To decrease oven temperature (for a cooler oven),
Press pad until a negative number appears in display.
5. Press OVEN CANCEL pad to save adjustment.
• Setting is saved if power fails or is disconnected.
heres a link to the entire manual if needed
http://shop.amana.com/assets/pdfs/literature/32103601.PDF
SOURCE: Furnace doesn't reach desired temperature
One of two things you can try. Do you own a volt ohm meter? Anytime your unit cycles short like it is doing the control circuit which on this one is 24 volts that engages relays and controls the gas valve to open and close. I am thinking the heat exchanger is getting so hot it is tripping the upper limit which for the most part is around 180 degrees. So next time it turns off take your ohm meter and with the power to the whole unit off. Either turn the breaker off or there is a light switch that is real close to unit turn it off. Undo the two wires to the gas valve and ohm them out. You should have continuity if you get nothing check each limit switch should have a couple. Undo wires to them and check. If you find one that is open more then likely the upper one. They are a safety device that keeps the unit from getting too hot.
There might be another option increase the speed of your fan motor to get the heat out of furnace quicker. Look at the circuit board notice the fan wiring going to it. The Red wire from fan is low speed look to see if it is on HEAT on the board. You should have 4 speeds to pick from you could take the black off of COOL and swap wires and test the unit by doing that. I'm going to put a solution on this so I can come back to it quicker. Even though we a just testing it for now. ken
SOURCE: cannot set heat setting by using "hold" feature
make sure it is not telling you room temp, some of the Honeywells, will display room temp over desired temp. check that, if it wont let you switch temp than buy a new one, if you dont have a heat pump a new cheap stat is around 20.00.
SOURCE: On our honeywell trolatemp universal minizone zone
sounds like a furnace problem - the zone control sounds right