LG Split System Air Conditioner Error code = C6 or CH06 LG AC Fault Definition = Excessive current at inverter DC power circuit - DC Peak Power
Flashing Light = 6
Display = Indoor Outdoor
Indoor Operation = SHUTDOWN
There are several things that can cause this,, first step is to check all wiring connections, but this can be pointing to a more major issue, the AC to DC transformer,,
It is a experienced tech kinda job
SOURCE: ERROR CODE ON AIRCONDITIONER LG ART COOL INVERTER MODEL NUMBER LSZ244VM4
Error C6 on lg cool art is common. you guy need a new CAPACITOR. cost $7.05c aud. it's 6uF 450vac.
take about less than 10min to install.
my lg model is lsz244vm-4, it's run well now.
SOURCE: ERROR CODE ON AIRCONDITIONER LG ART COOL INVERTER MODEL NUMBER LSZ244VM4
Hi,
The first thing i'll say is you will need to get it repaired by a technician and i strongly recommend you not to do it by urself.
Remote control units have diagnostic program in the
control, after 3 to 5 minutes of operating if the diagnostic
tools detect abnormal operation, then its shutdown the unit
to protect from damage. Thermistor sensor is one of the
parts that detect the operation of the unit. Out of range
or defective thermistor can shut the operation of the unit.
-
If your indoor and outdoor is clean start the
unit in cool mode and monitor the outdoor pipes. If your suction pipe is icing
or dry then your unit is under charge, but if your suction is cold and sweating
then the system is ok and sure that the thermistor sensor is defective.
-
Out of range thermistor sensor in both return
air and freeze up sensor can cause the tripping “off “ the unit.
Goodluck..
SOURCE: Lg invertor air con "neo plasma"
i have the same, only way to get goin is turn off at mains. ive now tried running on fan low .... got this tip from another problem and seems to work.
good luck
SOURCE: Bran new unit just got
First of all call the installer to check it. if you are the installer please write me to find the solution together.
6 - DC Peak Error
• Supplied power is not normal
• Comp Connector (CN-U,V,W) is disconnected or inserted to wrong
position
• Compressor is damaged (coil short) ? replace compressor
• Too much Refrigerant
• Defect in outdoor pcb assembly ? replace pcb assembly
Try turning power off to external unit, usually resets diagnostics and runs OK. If not PCB external unit likely culprit, replace!