Pramac Diesel generatorGSW 65 &GSW 80,in both generator we are facing problem that make them shutdown automatically and message displayed is SD AMP unbalanced? what should i do to solve the problem?

1 Answer

Bart Walker

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

  • Expert 206 Answers
  • Posted on Mar 15, 2019
Bart Walker
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

Joined: Dec 12, 2011
Answers
206
Questions
0
Helped
71517
Points
453

I don't know your equipment, but the unbalanced term may refer to too large a load connected to one leg of your split phase service. Go to your load panels and try to get the amps drawn by your loads to be more equal. You may be over taxing one leg and have available capacity on the other, assuming you are running a 110/220 V split phase output.

4 Related Answers

Anonymous

  • 474 Answers
  • Posted on Oct 31, 2009

SOURCE: need to change oil on my generator Pramac 16 hp

brigsandstratton.com

Ad

Anonymous

  • 1 Answer
  • Posted on Mar 16, 2010

SOURCE: portable generator head stopped making power

portable generator head stoped making power engine runs fine sircut brakers are fine

kel1guy2002

Kelly

  • 3740 Answers
  • Posted on Jun 26, 2010

SOURCE: perkins 3 cylinder powered pramac generator

Start looking at your safety circuits.

1. High water temp
2. Low Oil
3. Low water etc...

From the manual these are the protection circuits.

• Engine protection: low oil pressure, high engine temperature.
• Genset protection: under/over voltage, overload, battery charger failure, battery voltage out of limits,
under/over frequency, start failure.
• Circuit breaker protection: IV poles.
• Differential protection.


Any one of them will trip the fuel relay closed. What you may be able to do is disconnect one at a time each protection circuit and see when the fuel relay opens. (Make sure to reconnect each one if it had no effect on the fuel solenoid)

Once you isolate which circuit it is in then you can chase wires or change the bad switch.

Thanks for choosing FixYa.

Kelly

emissionwiz

Marvin

  • 85242 Answers
  • Posted on Jun 29, 2017

SOURCE: pramac diesel generator p4500 was running then stop how can i tell if any diesel in the pump

Crack open an injector line.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

We have a pramac genset equipped with a AC03 controller and time to time in AUTO mode it changes alone to MANUAL mode. Please, can anyone help? Best regards. FGaspar

You can changes to Auto mode.
Some generator has auto mode and manual mode. In generally, emergency generators have these two actions, when power grid is cut off, the generator will connect to machine automatically, then supply power to the machine.
If you need diesel generator set or more support, please visit at www.dieselgeneratortech.com
0helpful
1answer

Pramac electric start generator. Where is the choke, gas cut off, what is on/off switch in upper right of panel for?

Please see the operation manual.
If you have plan to purchase a new diesel generator set in future, please visit at www.dieselgeneratortech.com
0helpful
1answer

I require the valve clearance gap for a pramac p6000s diesel generator

If you need data of valve clearance gap of the diesel generator, you can check on the operation and maintenance manual. If still can not find, try to ask your supplier whom supplies the diesel generator to you.
If you need to have a generator set in future, please refer to www.dieselgeneratortech.com.
0helpful
2answers

Can I parallel 2 hyundia hy2000si generators together

No. You would have to synchronize them, and that's a difficult task.
0helpful
1answer

My diesel pramac P9000 generator engine is not starting even cranked for long time what is the problem

Check and replace the spark plug, clean filters and try again. If this doesn't fix it, it is probably the carb. Clean it and try a SMALL squirt of starter fluid
0helpful
2answers

Pramac 25 kva perkins encl diesel genset will not start red light on triangle on check list

Hello. Maybe you have solved your problems. But I still want to share the helpful article to you. https://www.dieselgeneratortech.com/diesel-generators/why-diesel-generator-fail-to-start.html

We are Perkins diesel generator OEM. Can provide 22KW to 2200KW diesel generator set with Perkins engine. https://www.dieselgeneratortech.com/perkins

perkins diesel generators-n5v1fnwbur1qlbncsxenjidv-1-0.jpg
0helpful
1answer

How to change oil in pramac gsw 50kw towable generator?

If you have a Yanmar engine...
There is a hose that is connected to the oil pan in place of the drain plug directly under the oil filter that will have an end cap. This hose is used to drain the oil into a waste container.
Download the service manual located at the address below and follow the instructions in the manual.
http://www.martindiesel.com/Documents/New%20TNV%20DIRECT%20Service.pdf
Hope this helps.
0helpful
1answer

Phase voltage is not same

What is your problem and what is the question?
1helpful
3answers

Portable generator head stopped making power

portable generator head stoped making power engine runs fine sircut brakers are fine
Not finding what you are looking for?

555 views

Ask a Question

Usually answered in minutes!

Top Pramac Electrical Supplies Experts

littlewheel

Level 2 Expert

122 Answers

Ngoro

Level 3 Expert

3523 Answers

john h

Level 3 Expert

29494 Answers

Are you a Pramac Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...