SOURCE: Ruud Silhouette II Fails to Ignite
sounds like you have bad flame sensor or the sensor is in a bad postition. To get eliminate the lockout turn the power off to the unit and back on again. Look at the circuit board light and see what the troubleshooting code is.
SOURCE: How do you change the air filter on a Ruud silhouette II furnace?
If it is a down flow, it will usually be found in the return air plenum just above the blower. You need to remove the front panels and look inside above the blower. You may need to remove a second door to access the blower section. If it is an upflow, remove the bottom door and look alongside the blower where the return air comes in.
SOURCE: Ruud Silhouette II Gas Furnace, the furnace lights
Bad or dirty flame rod.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
SOURCE: Ruud Silhouette II Gas Furnace, purges, lights
Flame sensor needs to be cleaned. turn off the furnace power switch or breaker. pull the flame sensor located in the burner runner section of the furnace. It will be easy to locate because it has 1 wire running to it. pull the screw being very careful not to harm anything else. get the sensor out. inspect it for cleanliness. clean the sensor with light grade sand paper gently. re-install the sensor plug the wire back on. restart your furnace and this should fix the problem.
CookHVACR
Testimonial: "thanks cookhvacr, took 15 minutes and it seems to be back to normal operation."
SOURCE: How do I clean the flame sensor rod for a Ruud
a dollar bill works well for cleaning flame sensors, too