When replacing a condensing unit , also must replace the dryer and vaccum the system for about 45 minutes and after that recharge it with scale for the right amount of freon written on the tag in the freezer .The normal operation pressures are between 50 to 60 psi for the suction side and about 350 no more than 375 psi for the high side.To calculate the superheat: suction line temp - evaporator temp= superheat.
I have reviewed your problem and it seems to me, that your head pressure is a little to high as well as your suction side pressure being too low.
It may be that your system has not settled down and or may be overcharged or could be due to a restriction in the cap tube.
I'm sure that you pulled a long vacuum on the unit and dryers has been replaced.
If the unit has had a burnout, did you flush the system or just vacuum..
Hope this information has been of some help.
Please rate....
P.S. you know, it could just be that the oil has not completely settled, but should with system running for a few hours.
Well, OK.
Here is where your mistake was.
1. If the compressor failure was a burnout, you should have flushed out the system before running a 1 hour vacuum.
2. One hour would be OK for a regular change out but once the oil brakes down, it becomes contaminated and as you know the oil is the hardest to remove.
3. I would never charge a system liquid, unless of course you were using a metering canister to inject the refrigerant.
I have always gone by the label when it comes to the charge and for my applications, I always flushed my systems with 502, after a burnout.
Sound like it may be one of those that just has to settle down.
You suction pressure should be right at 25 lbs for the temp of -10 degrees.
This afternoon the unit only pulled down to 20F head was down as well as suction. Iadded some 404A and got the head to 270 and suction to 10 still need superheat on this unit.
More info no burnout, dryer changed, vacuum for 1hour unit warm pulled to 167microns and held
new 404A charged liquid
As stated this was not a burn out 404A has to be charged as a liquid and flashed to a vapor and yes at 25 psiga 404a is at -10 F however to take in consideration the delta T of the evaporator the suction would be lower. My question is and has been from the very start what is the design superheat of this system and what are normal suction pressures?
I am beginning to feel as if your web site is not so good