Alarm and battery failure ; Powerware 9102 - Powerware 9120 UPS System

1 Answer

pravin bhavsar

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

  • Expert 348 Answers
  • Posted on Mar 08, 2010
pravin bhavsar
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

Joined: Oct 26, 2008
Answers
348
Questions
1
Helped
106345
Points
813

Open the screws and disconnect the battery look the voltage written on it and AH (ampere/hour) e.g.12v & 7ah and purchase same value battery and connect look carefully the +ve &-ve polarity of battery and connect in proper way

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

UPS Bypass mode failure

it looks like you have a faulty static switch
0helpful
2answers
0helpful
2answers

Alarm #191 open cell voltage powerware 9130

Remove the front panel plastic cover where the batteries are located, then plug the two connectors together, restart the UPS, and it should be fine.
0helpful
1answer

I have an Eaton 9355 20kva system. Theres an alarm #188 Bypass Failure and notice#105 Bypass Not available. The batteries are also not charging or the battery current is reading 0 amps. When the power goes...

Bypass failure is the same as your input unless you have a dual input. You lost power and the UPS did not hold the load because the batteries are bad. Replace the batteries and you will be ok.
0helpful
1answer

Alarm #191 open cell voltage powerware 9130

Alarm error #191 comes from a battery test, where batteries are put under load for 25 seconds. (If the alarm is unexpected, you might have enabled the periodic 30-day battery test.)

#191 is test failure for battery internal resistance. So, need to locate and replace the bad battery, then run the battery test manually. If batteries are good, make sure no battery connector is corroded or loose.
0helpful
2answers

Alarm #191 Battery test failed

Shut down the UPS and replace the batteries.
0helpful
1answer

I got charger failure alarm on display.

Unless new and hardly used - check the internal batteries. They might be worn out and fail to hold a proper charge. This to be able to deliver power when AC mains cuts out.
0helpful
1answer

I ave a powerware 9120 and get a Charger failure alarm

check your batery, may it was leaked, change it with new battery
1helpful
1answer

I have a Powerware 9120 2000 UPS battery failure message

Hi,

After you replaced the batteries did you perform a manual battery test?

If not do so.

Regards
Alan Hood
ami-man
UK
0helpful
4answers

Pw9120-6000

1st, the 9120 is a 700, 1000, 1500, 2000, 3000, 5000 or 6000 Va
if it is a 6000 Va that voltage sounds ok, and the ups as no problem, each battery will be around 12,75 Volts, it will be higher and the charging circle ends.
Not finding what you are looking for?

570 views

Ask a Question

Usually answered in minutes!

Top Powerware Computers & Internet Experts

Grand Canyon Tech
Grand Canyon Tech

Level 3 Expert

3867 Answers

Brad Brown

Level 3 Expert

19187 Answers

Cindy Wells

Level 3 Expert

6688 Answers

Are you a Powerware Computer and Internet Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...