You can set the temp for the unit to come on and it comes on and runs and cools for a few minutes then the compressor cuts off then the fan a little later. After a few minutes it comes back on and does the same thing. It never cools down to the set temp. The coils are wet but not frosting.

1 Answer

Donald DCruz

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Whirlpool Master 17,130 Answers
  • Posted on Aug 30, 2010
Donald DCruz
Whirlpool Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Jun 24, 2010
Answers
17130
Questions
0
Helped
3632667
Points
52372

Is the AC set on an energy saving mode. Together with this program if the thermostat is defective the same symtoms can appear. So please check on the thermostat and replace.
Since the compressor is cutting off the cooling does not take place to the extend that is set.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

Until now this unit has never had the compressor run without the fan. Is the compressor running without the fan a problem? If so, what can I do to correct it?

Possibly a tstat issue. Run system until satisfied, once satisfied indoor fan shuts down compressor still runs remove tstat face plate and see if compressor shuts down. Another issue could be a sticking contactor for compressor. With a meter you could check at the contactor to see if you lose your 24volts for cooling but contactor remains pulled in.
1helpful
1answer

Auto/On set to ON. Fan runs.

Sounds like the thermostat, the way to verify is to unplug indoor unit, remove thermostat, take pic of wiring with phone or label the wires as to the terminals. Carefully twist the yellow,(Y) Red (R) and the green (G) together. Plug the furnace back in, if the unit operates normally, replace the thermostat. I am basing this on the fact that the blower speed is changing. This could also be an anomaly within the circuit board in the furnace section, not likely though as the outside unit (condenser) is not controlled n by the indoor board unless this is a heat pump. hope this helps. D
0helpful
1answer

When I turn my window unit on, it will cool for 2 - 3 minutes. Then the fan turns off and the compressor continues to run for maybe another 90 seconds, then shuts off.

Make sure the filters are clean. Check what mode it is on as well. On heating, it is normal for there to be a delay before the unit starts up and then "run on" when turned off. Also check what temperature is set on it. If the temp is too high, the machine will cycle on and off as it thinks it has already reached the temp you want.
0helpful
1answer

4 ton Amana -heat comes on sporadic in spring and fall (Every season change) Heat worked through 20 degree weather. Thermostat at 74. Today is 100% humidity and 52 degrees outside and heat won't work. By...

Assuming this is a heat pump I'm guessing you have a bad temp sensor. Your outdoor fan is likely controlled by a temp sensor so it only runs as needed during heating. Fan not coming on and compressor still needs cooled therefore compressor protection kicking in?????

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

0helpful
1answer

Subzero 611 freezer not cooling

Could be but before that check if settings are working. Set the freezer settings to coolest and see if cools. If ok, set to desired temp.
0helpful
1answer

Air handler fan cuts on runs a few minutes and then cuts although thermostat is set to off.

your thermostat could be wired in to a energy recovery venilator which will bring the unit on for a certain amount of time every hour some thermostats have recirculate mode which will do the same thing to help filter the air
0helpful
1answer

Intermittent colling in Samsung Window AC

so your reported figures show that the unit is operating as planned
the closer to ambient temp the shorter it runs for
the further away from ambient temp the longer it runs for
when the desired temp is reached , the compressor will stop but the fan will continue to run to circulate air past the thermostat so that it will switch back on when the room temp reaches too high temp
and that is why it is recommended to set the temp at 25 C as that is the most economical temp to run it at
0helpful
1answer

The unit runs for a few minutes and completely shuts down

Without the model or make sound like a bad thermostat..check amps the the compressor and voltage... if the compressor is locking up or the thermostat cutting voltage to it..
Hope this helps
Not finding what you are looking for?

302 views

Ask a Question

Usually answered in minutes!

Top Whirlpool Heating & Cooling Experts

Ronny Bennett Sr.
Ronny Bennett Sr.

Level 3 Expert

6988 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66830 Answers

Are you a Whirlpool Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...