Steamist 11 KW Steam Unit SM11IM Logo
Posted on Dec 27, 2010
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
What size breaker does the sm-11 require 2-30amp or 2-60 amp?
Anonymous
Level 2:
Novelist:
  • Expert 185 Answers
  • Posted on Dec 28, 2010
Anonymous
Expert
Level 2:
Novelist:
Answers
185
Questions
0
Helped
74903
Points
375
You will need the 2-60A breakers. 11kw is 11,000 watts. Watts = voltage X Current (amperes) If we take this formula and change it around to calculate amperes it is like this. Amperes = watts / volts amperes = 11000 watts / 240 volts This is 45.8 amperes or let us say 46 amperes. The closest breaker that you have would be a 50 amp breaker 2 pole of course . 2 - 50. If you cannot get a 2 - 50 then a 2-60 is fine. I would run with a #6 copper wire, I would check with local code to verify the wire size in your area. Make sure that the unit is grounded as well. Minimum of a #10 wire, I would also check local codes as well. Enjoy the steam!
Need information on circuit breaker BR2100 60amp
Hi - I'm an electrician and can help you with your question.
A BR2100 circuit breaker is a 2 Pole 100 Amp (for the part number "BR2100", the "2" indicates the number of poles and the "100" indicates the amperage) circuit breaker. It can be installed in a single phase or three phase 120/240 VAC system panel that specifically lists the BR series breakers as acceptable for use.
A BR260 A BR2100 circuit breaker is a 2 Pole 60 Amp (the part number BR260, the "2" indicates the number of poles and the "60" indicates the amperage) circuit breaker. It can be installed in a single phase or three phase 120/240 VAC system panel that specifically lists the BR series breakers as acceptable for use.
It is not possible to have a BR2100 rated for 60 amps, 1 or 3 poles, or a BR260 rated for 100 amps, 1 or 3 poles.
It is not permissible to install any circuit breaker brand or type in any panel that does not specifically include it on a list of acceptable circuit breakers.
Circuit breakers are designed to carry 80% of the amperage rating.
To determine the load a circuit breaker can carry, multiply the circuit breaker amp rating by 80%.
This means that if you need to supply more than 80 amps, you cannot use a 100 amp circuit breaker. A higher rating is required. A BR2110 would be acceptable for loads greater than 80 amps, but less than 88 amps because the formula above says: 110 amp x 80% = 88 amps.
To determine the breaker size, determine the load (by measuring with a meter or obtaining amp rating of the load from the data plate) and multiply it by 125%. Using the same numbers in the example above; assume an 88 amp load. 88 amps x 125% = 110 amp circuit breaker. The 60 amp breaker is acceptable for up to 48 amps because 60amps x 80% = 48 amps. A 48 amp load needs a 60 amp breaker because 48 amps x 125% = 60 amps.
I hope this helps and good luck!
I have a new furnace and the breaker keeps tripping (20/30). It is a bryant westinghouse box. I think 200 amphes
1) You got a FIRE truck coming.
2) Wire is too small.
Problem is NOT circuit breaker.
3) Both 240Volt appliances on same breaker is a hazard, especially if space available in 200 amp service panel for more breakers.
4) Usually each 240V appliance has separate breaker.
5) Circuit breaker trips because of High heat on the wire.
If wire gets hot, it will start a fire inside the wall.
Electric code requires wire-size match breaker-size.
6) If you put larger amp breaker on same wire that is getting hot, then wire will get hotter.
Result: FIRE truck middle of night with folks jumping out window in glass-cut bare run across yard.
7) Each appliance has volts and watt rating on label.
EVERY appliance has label.
8) For example stove might be rated 8000 watts and 240Volt.
8000 watts divided by 240 volts = 33.3 amps
Stove would require 40 amp breaker and 8 gauge wire.
9) How to figure it out:
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/How-to-install-a-subpanel.html
10) Do same calculation for new furnace.
12000 watt furnace divided by 240 volts = 50 amps.
Use 60 amp breaker and 6 gauge wire.
11) Summary: fixya wants you to be safe, and buy stuff showing in the ads.
Use a bigger breaker ONLY when bigger wire is also installed.
Call furnace installer, the installer should know to check safe wiring before installing.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
What size wire and how does it hook to thr unit rpkb-036jaz
Look at rating plate on side of unit for Volts, Amps, Watts.
Volts x amps = watts.
If unit is 240Volts, then you need double-pole 240Volt breaker
If unit is 8500 watts at max power, then 8500 watts divided by 240Volts = 35 amps.
What size breaker for 35 amps?
When electricians figure load rating for breakers, they use the 80% rule.
40 amp breaker x 80% = 32 amp safe maximum load for 40 amp breaker. Use 8 gauge wire with 40 amp breaker.
50 amp breaker x 80% = 40 amp safe maximum for 50 amp breaker. I use 6 gauge wire with 50 amp breaker.
60 amp breaker x 80% = 48 amp safe maximum for 60 amp breaker. Again, use 6 gauge wire with 60 amp breaker.
How to connect wires to unit.
First of all, all outdoor HVAC units require power cut off located next to unit.
This lets the mechanic, or service tech turn power off to work on unit, even if the mechanic does not have access to main breaker box.
Next, open unit to see where wires connect.
If unit has wires, then connect both hot wires from 240 breaker to the wires inside unit. Connect bare ground wire to green ground screw.
If unit has terminals. The terminals will be labeled L1 L2. Connect each hot wire from 240Volt breaker to either one of the screw terminals. Then bare ground goes to green ground screw.
Copy following links for basic illustrations connecting wires to terminals, and to breakers, and selecting wire size.
http://waterheatertimer.org/How-to-wire-Tankless-electric-water-heater.html
I just bought a used Carrier FV4BNB006 Air Handler without elec heat (just the air handler itself) . I pulled down the Installation instructions, but dang if I can find the right circuit breaker size to...
Hi, when you get the unit, it will tell you the Min. and max amps on the units data plate.They normally run in the 30 to 60 amp range depending on the tonnage of the air handler. What I would do, is run your lines now, and pick up a 60 amp disconnect box. You can use what ever size fuses in the box that the data plate says. Very easy to find out. Good Luck,
Shastalaker7
A/C, & Heating Contractor
2helpful
2answers
2helpful
2answers
I have a campbell hausfeld 60 gallon compressor 20 amp motor what size breaker should be used
I am not a master electrician but I was an apprentice for 5 years and think you should be ok with a 30 amp breaker. anything less and you may be resetting the breaker when the unit first turns on. Dont forget 30 amp breakers will require # 10 wire or larger, #12 just wont do.
2answers
How do I run from a 100 amp main panel to a 60 amp subpanel, 125 from my house to the garage
See 60 Amp sub-panel image
Above image shows drawing of 60Amp sub-panel located next to main panel. Drawing shows #6 wire... 125' distance to garage calls for #4 wire. I ran #4 to my barn and have no problems.
Give thought to how many new breakers you want at garage.
See photo of subpanel that holds three 240V breakers
Using drawing as a guide. Replace existing 240Volt breaker with new 60 Amp breaker. Two hot wires connect to new 60 Amp breaker. Neutral connects to neutral busbar.
More space: You can free up space in main breaker box using a tandem breaker. Or by doubling up 2 lightly used 120V circuits onto one breaker. Do not double-up on 240 Breakers
Conduit: You want PVC conduit large enough to fit three #4 wires. Bigger conduit is easier to pull wires ... and maybe later ethernet wire, or alarm wire etc.
Ground wire: You can put a ground rod at garage and run #6 bare copper between sub-panel neutral-busbar and ground rod. Attach ground wire firmly with grounding clamp.
I want you to check with local electrical supply for exact code in your area concerning conduit requirements, grounding, and wire size. Tighten all lugs very tight against wire.
1helpful
3answers
What size breaker does the 11kw hayward comfort zone electric spa heater require?
It does make a difference as to input voltage. But usually at 11KW this would be a 220V unit and require a 50 amp breaker. 11,000W divided by 220VAC = 50 amps. 230 or 240V input the same 50 A breaker.
Thanks for choosing FixYa.
Kelly
1 or 2 circuits to create 2 phase?
How to explain this? your new drop in unit will require a 220v circuit capable of a specified amount of amps. Typically 40, 50 or 60. Should be noted in the manual and on the unit itself. If your original oven and cooktop were electric, then each one was probably hooked up to a 220v circuit. The problem is figuring out how many amps were supplied for each. The simplest way is the go to the panel and find the breaker for the old oven and cooktop and read the numbers (or amps) on the on/off switch. If either breaker has a number the same or greater then the drop in unit says it requires, then your all set. If the drop in unit says it requires 52amps and one of the breakers says 60 on it, your fine. If the drop in unit says it requires 44amps and the breakers are 30 or 40, then you got a problem. Usually a breaker is installed that is the maximum amps allowed for the size (thickness) of the wire connected to it. You CANNOT connected a 50a breaker to wire only rated for 40a. Note the size difference of wire connected to a 20a breaker with wire connected to 40a breaker. If the drop in unit requires more amps then the original units used, then a larger wire will need to be ran from the panel to the drop in unit (Not cheap). Now if the original oven used a 30a and the original cooktop used a 30a, then its possible ( 80% of electricians wouldn't do it because of liability problems) to use both wires together to create 60amps, but both wires (actually a total of 6 wires, 2-120v wires and 1 ground wire from each outlet) would need to be in the same outlet box for the drop in unit connection.. I could (and probably should) try to explain more, but I'de probably just confuse you more. GOOD LUCK!
8helpful
Wiring installation for ss5l5 IR 5hp 60 gallon compressor
A #10AWG wire can be use and 40Amp breaker can be use also. Your 5hp/230V/1/60hz motor amp is 30A.